There's some points being missed, and I'm startin' my own thread on this subject rather than keep runnin' other threads down sidetracks.
Argument - Modern stoves don't need or require a flue damper because they don't leak and the combustion air inlet controls the fire.
That may be true... but only if draft is within the design tolerances of the stove. Modern (secondary combustion) stoves are designed and engineered to work properly within a certain draft tolerance window. Typically they have two air intakes, primary and secondary; the relationship between those two is designed to work properly within that specific window. Although some users have claimed they can completely shutdown the air intake(s) on their modern EPA stoves, they must be missin' something... for a stove to pass EPA testing it must run (meaning the fire does not go out) at the lowest available user setting without smoldering the fire too much (particulate emissions must meet the regulations). So, in fact, a modern stove does leak... there's a built-in leak to insure compliance. Nearly every installation manual states the acceptable upper and lower draft tolerance... and, if required, most recommend a barometric damper to adjust said draft (the "suck" acting on the firebox... the "over-fire" draft).
OK, so let me ask a question... what is a flue damper??
Answer... a device installed in the flue pipe and used to adjust "over-fire" draft by reducing it (a damper cannot increase it, it can only reduce what exists).
Well boys, a barometric damper is a damn flue damper... so saying a modern stove does not need a flue damper flies in direct contradiction to most installation manuals/manufacturer recommendations (depending on conditions). Sayin' that every modern (EPA) stove, in every installation, does not need a flue damper is friggin' ridiculous... even the manufactures say they will need one (for peak performance) if draft ain't correct.
The two most common flue dampers are the manual "key" damper, and the (often recommended) semi-automatic barometric damper... they both accomplish the same thing, just in different ways. One reduces "suck" on the firebox by restricting pipe opening, the other reduces "suck" on the firebox by creating a leak in the pipe. Neither is ideal and without drawbacks. The manual "key" damper requires a bit of user thought, know-how, and yes, a learning curve... and an idiot can screw it up. The semi-auto barometric damper introduces cool air into the flue and pulls more air from the space being heated (that air must be made up from cold outside air)... and it does require periodic inspection, maintenance and adjustment. They both have their positives over the other also. One gives you instantaneous, total, variable control... the other handles the adjustment for you, but removes the convenient variable control. Don't overlook that convenient variable control... for getting a fire started, changing firewood species, even for a quick blast of heat when wanted.
What type or style of flue damper you opt for is a personal choice. What influences that choice could be any number of things. For example, if your chimney opening is subjected to constantly changing wind direction and speed, a baro may be a better choice so as to avoid constant damper adjustments. On the other hand, if your draft is relatively constant, and you prefer more control, you may find the manual damper more to your liking.
But either way... sayin' that modern secondary combustion stoves never require a flue damper is patently false. The manufacturers recommend flue dampers... they recommend the supposedly "fool-proof" type, but there ain't nothing "fool-proof", never has been, never will be. The fact is, unless the conditions are near perfect, a new-fangled stove will likely benefit more from a flue damper than an old style stove will. Unless conditions are perfect, your choice isn't whether-or-not to install a flue damper... the choice is which style to install.
The performance of any wood-fired appliance may be improved with a flue damper... but you'll never know if ya' don't try it.
There ain't no friggin' magic, never has been, never will be.
*
Argument - Modern stoves don't need or require a flue damper because they don't leak and the combustion air inlet controls the fire.
That may be true... but only if draft is within the design tolerances of the stove. Modern (secondary combustion) stoves are designed and engineered to work properly within a certain draft tolerance window. Typically they have two air intakes, primary and secondary; the relationship between those two is designed to work properly within that specific window. Although some users have claimed they can completely shutdown the air intake(s) on their modern EPA stoves, they must be missin' something... for a stove to pass EPA testing it must run (meaning the fire does not go out) at the lowest available user setting without smoldering the fire too much (particulate emissions must meet the regulations). So, in fact, a modern stove does leak... there's a built-in leak to insure compliance. Nearly every installation manual states the acceptable upper and lower draft tolerance... and, if required, most recommend a barometric damper to adjust said draft (the "suck" acting on the firebox... the "over-fire" draft).
OK, so let me ask a question... what is a flue damper??
Answer... a device installed in the flue pipe and used to adjust "over-fire" draft by reducing it (a damper cannot increase it, it can only reduce what exists).
Well boys, a barometric damper is a damn flue damper... so saying a modern stove does not need a flue damper flies in direct contradiction to most installation manuals/manufacturer recommendations (depending on conditions). Sayin' that every modern (EPA) stove, in every installation, does not need a flue damper is friggin' ridiculous... even the manufactures say they will need one (for peak performance) if draft ain't correct.
The two most common flue dampers are the manual "key" damper, and the (often recommended) semi-automatic barometric damper... they both accomplish the same thing, just in different ways. One reduces "suck" on the firebox by restricting pipe opening, the other reduces "suck" on the firebox by creating a leak in the pipe. Neither is ideal and without drawbacks. The manual "key" damper requires a bit of user thought, know-how, and yes, a learning curve... and an idiot can screw it up. The semi-auto barometric damper introduces cool air into the flue and pulls more air from the space being heated (that air must be made up from cold outside air)... and it does require periodic inspection, maintenance and adjustment. They both have their positives over the other also. One gives you instantaneous, total, variable control... the other handles the adjustment for you, but removes the convenient variable control. Don't overlook that convenient variable control... for getting a fire started, changing firewood species, even for a quick blast of heat when wanted.
What type or style of flue damper you opt for is a personal choice. What influences that choice could be any number of things. For example, if your chimney opening is subjected to constantly changing wind direction and speed, a baro may be a better choice so as to avoid constant damper adjustments. On the other hand, if your draft is relatively constant, and you prefer more control, you may find the manual damper more to your liking.
But either way... sayin' that modern secondary combustion stoves never require a flue damper is patently false. The manufacturers recommend flue dampers... they recommend the supposedly "fool-proof" type, but there ain't nothing "fool-proof", never has been, never will be. The fact is, unless the conditions are near perfect, a new-fangled stove will likely benefit more from a flue damper than an old style stove will. Unless conditions are perfect, your choice isn't whether-or-not to install a flue damper... the choice is which style to install.
The performance of any wood-fired appliance may be improved with a flue damper... but you'll never know if ya' don't try it.
There ain't no friggin' magic, never has been, never will be.
*