Ducted wrong
Your stove is ducted wrong your never going to move any heat as its currently hooked up.
You have 2 options
1. Tie the Hot air side of the wood stove to the cold air side of the furnace and allow furnace blower to move the air to the house. That is the normal hack way. You will need a secondary thermostat to cycle the furnace blower on and off as needed.
2. Better way is to hook up in complete loop by ducting the cold air to cold air of furnace. And Hot air of the wood stove to hot air of furnace. Then isolate furnace with flopper. However you will need a much bigger blower than 500 cfm and you cant do it with 2 small rounds you will need a plenum.
Mark