Your probably right,a new radiator can cost just as much as a HX.I would not want to buy a used one.
The first time I set up a boiler system all I was controlling furnace squirrel cage. I was using a hot water tank as the heater, grundfos pump and diesel truck radiator. I knew that a standard t-stat would not handle the wattage (voltage times amperage) of the blower system.
Standard household t-stats only run at 24 volts. Blower motors in general are 110 volts. You can run a baseboard heater t-stat. These units in general, baseboard t-stats, can either be set up as either 110 volt or 220 volt.
The only draw back to running the t-stats is that you have to run 14-2 wire or greater to control the blower unit. 24 volt t-stats usually only run 20-4 wire. The baseboard t-stats are more money, but you are not constantly having to replace them.
HTH
Glenn