I just put in the manifold system this year. I would prefer more flow thru the water to air HX. but it does ok so far. but its not really cold yet.So 2 gpm is getting the job done? That is good to know.
I just put in the manifold system this year. I would prefer more flow thru the water to air HX. but it does ok so far. but its not really cold yet.So 2 gpm is getting the job done? That is good to know.
something isn't adding up. my heat output with my boiler is much higher than my 100,000 btu high efficiency gas furnace. so either my high efficiency furnace is 10 percent efficient. or I'm getting more than 2 gallons per minute, thru my 2 gallon per minute manifold. or your numbers are off. maybe you meant btu's per minute not hour?
(here is a link to my manifold) http://r.search.yahoo.com/_ylt=A0LEVrdVU05WqrgAfesnnIlQ;_ylu=X3oDMTByOHZyb21tBGNvbG8DYmYxBHBvcwMxBHZ0aWQDBHNlYwNzcg--/RV=2/RE=1448002517/RO=10/RU=http://media.wattswater.com/download/WR_WattsRadiant_Catalog_FullLine_04_Manifolds-EN.pdf/RK=0/RS=s8_oRfCnplwb0y_6C77nuzp1qkk-
ah-ha!!!! I got it I came up with the reason why the numbers aren't adding up. I'm measuring my incoming water and my outgoing water. I have a manifold set up that sends water to 4 different sources. only one of those sources is the forced air furnace. so the cold air from the furnace is being mixed with the (relatively) hot water of the plate HX, (which doesn't cool the boiler water unless the faucet is running) the base board heaters, (which often don't call for heat) and the clothes dryer (which also often doesn't call for heat). so thats why we aren't getting an accurate reading. really what I need to do is put a temp gauge on the return for the cold water on the water to air HX for an accurate formula.1 btu = 1 lb. of water 1 °F.
1 gallon of water = 8 lbs.
2 gpm = 120 gph.
So, 20° x 8 lbs x 120 gph = 19200 btu/hr.
That's what I come up with.
Second, regarding your system. As I read it, your main problem is on the geothermal heating side, both with expense and comfort. The best way to use a boiler with a geothermal system is to put it in the field loop and run it during heating season to maintain loop temperatures at a point that allows full output from the Geo system, which keeps the system from using its resistance heat. The next best way is to use a HX in the air stream to raise supply air temperature for occupant comfort. In your case, this could be accomplished by piping your boiler so that it supplies a storage tank at a constant temperature, which then feeds a pair of heat exchangers, one water-to-water on the ground loop and one water to air in the discharge air stream, both heat exchangers fed by dedicated pumps and both flow-controlled via thermostatically controlled three way valves. You could then disconnect your resistance heat, your geothermal system could run efficiently, and the air would be warm coming out of the ducts.
Third, regarding radiant cooling. I like Siegenthaler, but radiant cooling using groundwater in the Midwest is a pig in a poke, because our dewpoint are too high for about 360 days a year. If you don't have water cold enough to get air below the dew point necessary for comfort cooling, which is 55 degrees F, all you're going to be is clammy, and without a chiller you're not getting that. Spend your money on fixing your geothermal cooling and be done with it. Geothermal systems should not be difficult to diagnose and repair. If your current guy is struggling, you need a different guy.
Good luck, whatever you do.
Good morning,
I do this for a living. A couple things for you to be aware of:
First, regarding a heat source. I recommend the use of a condensing boiler, but be aware that when using an air-to-water HX the discharge temperature of the air is going to approach the temperature of the boiler water. If your boiler has satisfied during an off cycle of the air handler, when it cycles back on it's going to take a period of time for the discharge air temperature to warm up and stabilize. Large commercial systems don't have this problem, since they typically have multiple loads and high system volume. The solution for a small system is a storage tank, and it's almost always going to be bigger than you think it should be. If you put in a condensing boiler, be very, very, very attentive to water chemistry. Because the heat exchangers are constructed with relatively small passages to allow extraction of the last little bit of heat, and they are very prone to fouling if you have water quality issues
Regarding your current system, there are only about six moving parts in a refrigeration system. The principles are consistent and not terribly complicated. What is your system doing or not doing that is such a novel problem that four people cannot figure it out?
Well, here's what I would do if I were on site:
1. Throw an amp clamp on the water pump to make sure that it's moving water. Hopefully somebody put pressure gauges on the inlet and outlet, so with differential pressure and amperages you can Take a look at the pump curve and it should tell you what the flow is, if it's flowing.
2. Gauge up to the system and see if it has any refrigerant left at all. If it does, reclaim it so that I could put it back in when I'm done fixing the leak. Hopefully water doesn't squirt out of the Schrader valve. If it does, the refrigerant to water HX is bollocks and now you're in a trick bag.
3. Pressurize the refrigerant side with dry nitrogen and a tracer of 22 so my leak detector will work. Use a refrigerant detector/ultrasonic detector/soap bubbles to find the leak.
4. Fix the leak
5. Re pressurize to 300psi with nitrogen and leave it overnight.
6. Dump the nitrogen, change the filters, evacuate to 500 microns.
7. Weigh the factory charge back in. 22 is expensive, but it's not crazy. Don't be scared.
8. Start the system and check pressures, set superheat as needed.
It's not complicated. "Don't work on geothermal systems." Who says that?
It doesn't get any better when it's just a simple propane furnace with heat pump. A total of 4 different guys and I gave up. Bought a set of gauges, dye, jug of 410 and went to town on my system. 5 minutes in I found the elusive leak... Another hour and the system was charged and cooling this spring. Worked like a dream all summer but now the heat pump doesn't function..... Switched to propane and moved on. I don't have time to diagnose it and have spent about the same money as you on incompetent techs that never could fix my heat pump.... Hasn't worked since the first day it was installedBallpark what would that cost? Want to make a trip to NE Ohio? All anyone around here wants to do is sell me a new one. I've been through the web, BBB, Internet searches, Angie's list. Even the people who install lots them don't seem to have a good track record for fixing them. I'm sure I could keep trying random people and maybe find someone to fix it but it costs me $100 every time someone comes out. I'm getting tired of paying to explain to some jag off how a geo works.