I've don't more drilling down. I put a thermometer on the supply pipe at the boiler. It is 162 and inside at the exchanger it is 160. The boiler temp was at 187. I moved the thermometer sending unit up the boiler near the built in thermo wells for the boiler Stat and got 187. It seems that the lines aren't the culprit. The issue is the boiler water is not leaving the boiler at the correct temp. I changed the circulator cartridge to a new one and snaked the ports which appeared clear. I opened the valve with the circ off and water gushed out. Any ideas on why the water temp on the supply line is so low.