Here's the first and most important thing to figure out: why is your exchanger outlet so much cooler than your boiler inlet? If you truly only have one circuit (out to the exchanger and back to the boiler) then if there is flow what you are reporting is an impossibility. That leaves two possibilities: either your measurement is wrong (bad thermometer, bad operator of same) or you have no or very little flow, which allows the ambient conditions in the box to fool whatever Dollar Store thermometers are in there. My money is on no or very low flow, brought about by a fouled exchanger, which was caused by long running at high temperatures and low velocities. In any heat exchanger, I have always been taught that the most likely place for fouling to occur is the highest temperature, lowest velocity point, which in your case is your 1 1/4 connection HX on a 1" line.
You can prove this with an amp clamp by measuring current draw of the circulator and comparing it to full load amps on the motor. If you do this, I will bet the donut against the hole that you are well under the FLA.
If you don't have a clamp, isolate the heat exchanger, break the discharge connection, and then open the inlet valve and run the discharge in a bucket. When you do this, measure the rate at which the bucket fills and compare it to what it should be flowing- which if I recall is about 8 gpm. Watch the thermometers when you do this, because if you establish flow they should start moving the right direction.
Good luck.
You can prove this with an amp clamp by measuring current draw of the circulator and comparing it to full load amps on the motor. If you do this, I will bet the donut against the hole that you are well under the FLA.
If you don't have a clamp, isolate the heat exchanger, break the discharge connection, and then open the inlet valve and run the discharge in a bucket. When you do this, measure the rate at which the bucket fills and compare it to what it should be flowing- which if I recall is about 8 gpm. Watch the thermometers when you do this, because if you establish flow they should start moving the right direction.
Good luck.