Can you verify the owb guage is reading right? With an IR gun, you can usually get a reading on the fitting it's screwed into. Might have to spray a spot of paint first. But we also don't know if your IR gun is accurate.
If the OWB guage (which is in the upper part of the boiler) is right, and you only have 142 water at the bottom, that means you do not have enough flow through the boiler. Even if the aquastat is out somehow, playing with the aquastat won't make the water at the bottom get much hotter. It needs flow through the boiler to make that happen. I would not mess around any more with the aquastat until you get temps at the bottom closer to what they are at the top. The aquastat could be in a hotter part of the boiler than the guage.
I am leaning to plugged HX, but we still don't know what you did when you 'bypassed' it.
If the OWB guage (which is in the upper part of the boiler) is right, and you only have 142 water at the bottom, that means you do not have enough flow through the boiler. Even if the aquastat is out somehow, playing with the aquastat won't make the water at the bottom get much hotter. It needs flow through the boiler to make that happen. I would not mess around any more with the aquastat until you get temps at the bottom closer to what they are at the top. The aquastat could be in a hotter part of the boiler than the guage.
I am leaning to plugged HX, but we still don't know what you did when you 'bypassed' it.